1 hour ago, Larry Buskirk said:

neutral be bonded to ground

What does that look like Larry? Like a physical bond? A weld or something? Thanks

  • Like 2
Posted
8 hours ago, Larry Buskirk said:

I'm not sure if it's code everywhere, but Wisconsin requires the neutral be bonded to ground to prevent the  occurrence of everything taking a 220V hit if the neutral should fail. Makes sense to me considering neutral is at ground potential. 

It’s in The NEC, but if that bond occurs in the meter socket, and the neutral lets go in the panel, well...... you’re getting 220 volts to everything in the panel. Doesn’t happen often, but enough that we are all aware of it.

Posted

Thanks for the great explanation Artie.

  • Like 3
Posted

@Artie,

I forgot to mention that the inspector had me remove the bonding screws in the indoor sub panels, which I did right in front of him. The specs in the code weren't very clear about the sub panels. The inspector checked his code book, and said that the ground to the outside sub panel was to code which surprised him. That was better than 15 years ago though so things might be different now.

  • Like 3
Posted
1 hour ago, Artie said:

I’m not saying I’ve ever cut one, BUT..... make sure you peen the head of the rod good, iff’n you wuz to cut one LOLOLOL.

All four of mine are full length, I can't remember how many tries it took to finally get them that way. :WonderScratch:

Posted

I do not know code but I have never seen more than one ground rod in MS on homes we have had. But now I will have to look.

Posted

Not all states go by NEC. Many make changes to it. Massachusetts does, then passes it as law. It becomes Mass state code. 1 ground rod is sufficient, but you must prove 50 ohms or less resistance (I believe it’s 50, wouldn’t swear to that number), if you just install 2 rods, no resistance metering required. I installed two on a service change I did for my Grandfather’s neighbor on Plum Island (relative of Alan Shepard the astronaut). I threw the rod into the sand, it went more than halfway down, I hit it with a 3 pound sledge, and it disappeared into the sand. I had to dig down to find the end and pull it back up. I put two rods in the sand, and when it’s dry out, I wouldn’t trust that ground, but it met code.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...