December 10, 201114 yr comment_36809 OK I didn't pay too much attention to the plug type and amps in planning to convert this table saw to 110 volts. It came pre-wired for 220 volts. The owner manual tells how to do that. I have one plug on the wall for others tools that are 110 volts. In converting the table saw to 110 volts, the manual says to change the power cord plug and the wall plug to 5-20 which is different than the usual 110 volt plug. Also in reading the manual the FULL LOAD CURRENT RATING at 110 volts is 16 amps. My question is would I be tripping the breaker at when I run this saw with say shop vac or electric heater? Can I even run the electric heater or any other tools on the 5-20 type wall plug. It would look like this one NEMA 5-20    20-Amp   Grounded                 Wayne E Report
December 10, 201114 yr comment_36811 Wayne, you probably won't kick a 20 amp breaker if you're running a saw and turn on a shop vac, however if you're running a shop vac and turn on the saw you may. The amperage spike in on ionital startup. I'd advise that you leave the saw on a dedicated breaker if possible.Ron DudelstonAbove and Beyond WoodWorks Report
December 11, 201114 yr Author comment_36810 Ron Dudelston said:Wayne, you probably won't kick a 20 amp breaker if you're running a saw and turn on a shop vac, however if you're running a shop vac and turn on the saw you may. The amperage spike in on ionital startup. I'd advise that you leave the saw on a dedicated breaker if possible.Ron DudelstonAbove and Beyond WoodWorksRonThat sort of what I figured. Just needed someone else opinion.ThanksWayne E Report